saint elmo
Trainee
hi im redoing the bathroom and the 9.5kw shower is on this cable which has burnt at the connector block at some point its on a B32 MCB
im not sure what size this cable is, measuring the cable width it looks to be 6mm2 measuring the conductor looks to be a 10mm2
the diameter of the individual conductors is between 4-5mm
the width of the overall cable is about 14mm
the earth is significantly smaller, slightly thicker than a 2.5mm2 conductor
pictured next to 2.5mm2 cable for comparison
when i put everything through the IEC calculator it says the earth size should be the same as live and neutral cable wrong anyway?
With twin and earth cable, the cpc (earth) is smaller…. Perfectly ok.
I would say it’s 6.00mm as it’s a solid cpc (2.5mm size)
With 10mm, the cpc is stranded (4.0mm size)
just curious, but where was that connector block?
I just find it strange that a plastic connector is screwed down like that…. And I know that’s the way everyone does it.
Metal screw possibly cutting into the plastic, reducing the insulating material and creating a weakened path between the live copper and the cpc through the screw.
Not the problem here, I should add.
This is simply a loose connection causing heat
I’m 99% sure it is looking at that, as above comparing the 2.5mm cpc with the 2.5mm T+E it looks spot on.
(If you have a micrometer you can just halve the measurement of a single strand, multiple by itself then PI, then by the number of strands (usually 7) to double check.)
Just a thought…. Have a look on the grey sheath of the cable, it sometimes has the size marked into it
Instead of mucking around cutting strands etc, try and work out the cable route distance, measure the resistance, look in the OSG or 7671 and check th /e mili ohm per meter and work it out from that. just a thought.
If he doesn't know whether a cable is 6mm or 10mm then I suspect he's not going to have a copy if BS7671 and an Ohmeter. I don't think the OP is a spark Pete.
He says he is a trainee electrician
The OPs profile says he is a Trainee Electrician and has 2365 so deductions would say he should own or have accessv to BS 7671 BUT YOUR POINT IS A VALID ONE
Ah sorry, my mistake. Been a long day!
I have a thing about electric showers. I dont like using them and would never ever have one
i hate showers full stop. wirth a bath, I can have a smoke, JD perched on the bath rim, er' indoors to wash my back (in between JD refills), roll on next Xmas.
For me as well Mate been down to Bath to sort out some faults for my sister in law, knees are shot as is my back, gets home and my cooker is busted simple to fix though lamp gone took out cart fuse in plug top, didn't help me knees though
to clarify i did 2365 part time college last term ive not worked with a spark and what we covered in practical was mostly only lighting circuits and sockets never touched anything bigger than 2.5mm other than SWA
missed a lot of lessons due to college closed with covid too