RyanCheetham

Morning guys, today i have to run in a new supply for an induction hob. It will be ran externally in conduit for around 5m then it will come into the kitchen and i am going to clip direct to the wall behind the units, the kitchen is U shape and the hob is on the opposite side of the room to the cables point of entry. My original plan was to chase the screed and go straight across to the hob, however going around the wall is far easier. My question is if i had of chased the floor, would plastic conduit of been satisfactory protection before making good or would it need to be more robust? The floor chase would of been about 2.8m long
 
Having seen some of the power requirements for these induction hobs ( the last one I did was rated at 10.5 Kw ) what size conduit / cable are you hoping to use
 
Ive pulled a 6mm in through 25mm conduit as that is what was specced by the electrician i am working with
 
Yeah i thought as much but i as i have never chased a floor as i dont like the idea it is an issue i thought i should raise just in case. Thanks
 
Yeah i thought as much but i as i have never chased a floor as i dont like the idea it is an issue i thought i should raise just in case. Thanks

Youd be there all day chasing the floor!...

I see it quite often in workshops actually(Older ones anyway), metal conduit installed in the floor to machinery...
 