You are using the same size cable: For example table 4E4A: ref method D, 35mm cable, 115A.
Lets forget about VD and all the other factors for now, but for my examples you could use 35mm cable.
The lengths are the same, the cables are the same size so the resistance are the same.
But higher resistance individually than the larger single cable that they are being compared to...
Lets assume large cable is 10ohms
Smaller cables are 20ohms each
The two smaller in parallel do not equal half of the larger (in this example the overall is the same 10ohms)
All the cable in the ground is interested in is how much current it is carrying and how quickly it can dissipate heat - this will obviously be hindered by an adjacent cable also giving off heat (regardless of how each cable is connected further down the line)
Something to bear in mind is that the current capacity/unit csa increases with decreasing csa.
eg, Two 25mm[SUP]2[/SUP] can carry >2x current than that of a single 50mm[SUP]2[/SUP].
So much so, that even applying a two cct de-reating factor to the two cables, the CCC is still greater than that of the single larger cable.
Try it with some figures off Table 4D1A.
Yes but the issue here is sizing the smallest cable possible to carry 100A while at the same time ignoring grouping.
Another thing to bear in mind chaps is the OP of this thread has multiple smaller ducts (by mistake), so may not be running his cables together physically, ie. seperate cables in seperate ducts.
Intersting thread though.
lol - I think it was posts 4-5 that derailed the thread train!
Looks like the OP didn't get back. Wondering if he has sorted it out?
I thought the thread shifted from the original multi conduit to 'not having to use de-rating factors for a single circuit parallel route'? Or has it shifted again...
Not sure Spoon, The OP was looking for an answer to his problem before I had inadvertently side tracked it #5. lol
Looks like he was a bit vague about what he actually needed. Its hard to help out when you dont have all the info.
Hopefully he should get his answer by reading posts 5 onwards...
I think Eng and Tony will probably back me up on this when I say that if the OP is dealing with having to carry different cables through different routes, therefore possibly ending up with different lengths and so on, that they wouldn't really be identical conductors which is an integral condition for parallel supply; at which point I think you probably would have to take a common sense approach to how best to apply any derate factors. That being said, if your cable resistances (as installed) were within a nats todger of each other then I don't think I'd be overly concerned - again, some common sense would need to prevail.
All circuits in any installation are in parallel - supply live enters building, splits and feeds circs, returns to neutral bar and exits on supply neutral...
You have three single phase circuit feeding 3 equal loads, lets say 100A each in same containment - this is still 3 circuits in parallel - can you then ignore grouping?
If the separate cables do not derive from a single OCPD etc, and do not terminate at the same point of load, then it isn't a parallel supply. So what you're describing isn't a single paralleled circuit, it's 3 separate circuits and therefore those circuits will be subject to a grouping factor!! Unless of course they comply with conditions where the grouping factor can be ignored!!
In simplistic terms, if the paralleled cables start and finish from the same single points at each end of the circuit then they are classed as a single circuit and you don't apply a grouping factor to a single circuit. Other derating factors and the cables installation method do apply, and will if designed correctly, adequately look after the circuit cables....
Respect your opinion on this but I think we may have to agree to disagree - regards
The point is that if they are the same (which is the definition of a parallel supply) they have no affect on each other, hence why you don't need to apply derate for that reason. Any other aspect of interference from external sources is acting on them both equally, so can be counted as one. If I placed another conductor from a different circuit that was running at say 70 degC, then obviously there is going to be a transfer of heat from that new conductor to the originals as would be the case if they were a single cable.
The reason for using parallel conductors is simply that you have a greater surface area of conductor which means you have a more efficient system - 2 x 40mm is a greater area than 1 x 80mm (do the maths if you don't believe me).
No no no!!!
Not when they are touching each other, school boy maths/physics. If there's a significant gap between them, fair enough.
I'm going with my theory in post 32.
Trouble is it contradicts the old R = (rho x l)/csa
Sorry for not getting back sooner on this thread, it's made a real interesting read and given me lots of thoughts.
For what's its worth, it'll be an equal load, same distance and same connection points. A proper parallel circuit
. It's actually a large three phase distribution circuit, but due to the complexity of the steel work in the concrete pour, the contractors installed five small ducts instead of a decent single one.
I didn't actually put all the details as I didn't need, or expect anyone to do the cable calc for me.
Im actually only going to apply the basic correction factors. Although it's a decent sized supply, it a very short distance. About 6m. The ducts are separated, short and equal.
I'm actually working out the cable size as a single cable ducted, then splitting it by the minimal number of cables baring in mind the size of the ducting and then checking and verifying the individual cable calcs again.
If that all makes sense, I think I'm attacking it the right way.
What sort of supply current are we talking about here??
If the ducts follow the same route and are essentially the same length, then it shouldn't be a problem. The main problem you are going to face, is the terminations and conductor connections at each end of the parallel supply.... You're probably going to need extended connection bars/points, ...if you have room for them that is!! lol!!