Also check what the OCPD requirements are, it might be each charger needs its own protection so you would be needing either 6 cables from the DB, one per charger, or a sub-DB at the end to distribute power.
I am no expert on EV chargers but I would be very surprised if 22kW units are not 3-phase, and also need neutral, so you would be looking at 4C cable for the feeds.
Also are the two cables you mention going in separate ducts, or shared duct? Then you have to allow a grouping factor as well as the buried-method de-rating.
I am no expert on EV chargers but I would be very surprised if 22kW units are not 3-phase, and also need neutral, so you would be looking at 4C cable for the feeds.
Also are the two cables you mention going in separate ducts, or shared duct? Then you have to allow a grouping factor as well as the buried-method de-rating.