I need a cable for 10kW/44Amps Shower. 10M run

TLC Catalogue for T&E 6242Y recommends 10mm upto 53 Amps. Doncaster Cables online calc reckons 4mm.
Draka online calc agrees with TLC. Common sense also says 10mm.
What have I got wrong for Doncaster to suggest 4mm?

Thanks
Michael
 
Why not buy a cable calc programme there's plenty of software out there but even then you still need to do a manual check with the regs book now and then to check the cable selections
 
No offence intended, but the first thing any electrician will tell you when asking about a 10kw shower is that you need at least 10mm. Are you actually an electrician mate, as this is a notifiable job?
 
I remember looking at that Doncaster tool a while ago and it seemed to be blatantly wrong. I was sad cos I really like Doncaster cable, I find it the easiest to work with, although it can be overly powdery inside. Not that that has anything to do with their kak cable calculator of course. Just saying. :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent

Thread Information

Title
Cable Size
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Michaelwgroves,
Last reply from
Michaelwgroves,
Replies
20
Views
2,863

Advert

Back
Top