I need a cable for 10kW/44Amps Shower. 10M run

TLC Catalogue for T&E 6242Y recommends 10mm upto 53 Amps. Doncaster Cables online calc reckons 4mm.
Draka online calc agrees with TLC. Common sense also says 10mm.
What have I got wrong for Doncaster to suggest 4mm?

Thanks
Michael
 
Hi Mate

The cable calc on the TLC calculator [Voltage Drop Calculator]gives a cable size of 10mm


[TABLE="class: results"]


[TR]

[TD]Required Cable Size[/TD]

[TD]10 mm[/TD]
[/TR]

[TR]

[TD]Voltage Drop[/TD]

[TD]1.91 Volts.[/TD]
[/TR]

[TR]

[TD]Percentage Drop[/TD]

[TD]0.83%[/TD]
[/TR]

[TR]

[TD]Current Load[/TD]

[TD]43.0 Amps[/TD]
[/TR]

[TR]

[TD]Max Cable Load[SUP]*[/SUP][/TD]

[TD]45.0 Amps[/TD]
[/TR]

[/TABLE]
 
Okay, latest update. The Doncaster cable calc is based on cable type BS5467 (Armoured), not T&E 6242Y as I first thought. It's in the small print. That said, they are correct.
I bet there it not many DIY'ers that will spot that subtle difference, or even electricians!
Be warned.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent

Thread Information

Title
Cable Size
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Michaelwgroves,
Last reply from
Michaelwgroves,
Replies
20
Views
2,863

Advert

Back
Top