Hi Mate

The cable calc on the TLC calculator [Voltage Drop Calculator]gives a cable size of 10mm


[TABLE="class: results"]


[TR]

[TD]Required Cable Size[/TD]

[TD]10 mm[/TD]
[/TR]

[TR]

[TD]Voltage Drop[/TD]

[TD]1.91 Volts.[/TD]
[/TR]

[TR]

[TD]Percentage Drop[/TD]

[TD]0.83%[/TD]
[/TR]

[TR]

[TD]Current Load[/TD]

[TD]43.0 Amps[/TD]
[/TR]

[TR]

[TD]Max Cable Load[SUP]*[/SUP][/TD]

[TD]45.0 Amps[/TD]
[/TR]

[/TABLE]
 
If an online calc is that blatantly wrong, then this could be disastrous for all the DIY'ers out there who haven't got a clue (and some so-called electricians).
 
which is why DIY should be limited to replacement of accessories and gardening.
 
Okay, latest update. The Doncaster cable calc is based on cable type BS5467 (Armoured), not T&E 6242Y as I first thought. It's in the small print. That said, they are correct.
I bet there it not many DIY'ers that will spot that subtle difference, or even electricians!
Be warned.
 