Discuss Cable sizing calculation in the UK Electrical Forum area at ElectriciansForums.net
Happy New Year all.
Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run in the attic, 6m is run clipped direct down and across a wall and the remaining 10-11m will be buried underground in a 2 inch duct to the car charging unit. My calculations tell me I require a 10sq cable. However, whenever I've seen other sparks install a 7kw car charging unit, it's usually a 6sq cable run. Granted the runs would be a bit shorter.
Any thoughts or tips on this please?
and what cable will you use ?
depending on de-rating factors, it may be possible to do the run in 4mm swa. assuming a 5% voltage drop.
do you want to share your calculations for a double check?
To be honest James I use an app- Electrical Calculations. It auto calculates the cable size once you enter the specifics/parameters. Voltage, load, PF,
length of run, max volt drop, method of install, ambient temp, conductor, insulation etc. Not good practice I know to be putting my faith in an app for this.
230v, 7.4kw, 0.9 PF, 30m line run, 4% volt drop, I changed the method of install to buried directly in the ground, ground temp of 10° and it suggested a 6sq cable
Reply to Cable sizing calculation in the UK Electrical Forum area at ElectriciansForums.net
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
I have a run of cable where 12% is buried in ducts, the rest is on perforated tray, what are the limits on amount of cable buried when sizing cables?
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...