davesparks
exactly then halved = obv not 2mm as I stated.
Guess I'm trying to understand how we can calculate the main earthing conductor size then half that for bonding.
Was trying to understand the way it could be calculated, I know the regs say 6mm FYI.
Maybe I worded things not too great...
Earthing conductor size can be calculated using the adiabatic equation.
Main bonding normally can be half that size, but not less than 6mm and not normally more than 25mm.
So if your earthing conductor needs to be 25mm you need a bonding conductor of 12.5mm minimum so would install 16mm as it's the next nearest size above that.
If your earthing conductor needs to be 6mm then your bonding conductor would also need to be 6mm due to the minimum size requirement.