You not got a recycling bin for waste paper.C2 according to napit codebreakers book. Their opinion not mine.
You not got a recycling bin for waste paper.C2 according to napit codebreakers book. Their opinion not mine.
Why so harsh on the book. It's very difficult to decide what to put on the eicr personally I like to avoid that bs and defer to an "authoritive source"You not got a recycling bin for waste paper.
I'm not sure. Why is 25mm specified at all?The code breaker book advises a C2 code for tails that are not the minimum required 25mm.
I mean where in bs7671 states that tails must be 25mm?
What if you have 16mm tails? Why is that a C2 if they are acceptable for the load they are connected to and satisfy the requirements for fault protection?
That’s my point.I'm not sure. Why is 25mm specified at all?
Maybe it would be good to know why the 25mm is specified, if we understood that we might understand why the c2 is in the book.That’s my point.
Anybody going to contradict this?Is it not actually better for various reasons. You can't do a live test for zs without bonding connected which will give you a lower value. However building works may permanently remove that parallel path.
If you use ze + r1 + r2 you get the highest possible value which will be more resilient.
No?
I think that what you're saying is reasonable however we always test sockets with a plug, at least I do, so that covers that. Then you have lights, switches and other devices which are tested at the terminals to test the connection not the device.Personally speaking I always prefer to measure Zs as this is the only test that confirms the complete circuit including protective devices. There’s always a possibility that you can have a high resistance accross a device that would result in a high impedance at the end of the circuit. This will never be found by calculation.
Agree but to get your r1 + r2 reading-the curcuit needs to be switched off,so why not a zs testGN3 states that calculating you Zs is perfectly acceptable. Almost seems to advise it over live testing.
Zs test is a live test. It also includes parallel paths which might be removed. There can be parallel which shouldn't be removed and there's a procedure for managing them.Agree but to get your r1 + r2 reading-the curcuit needs to be switched off,so why not a zs test
Dno on our new build sites stipulate 25mm conductors with a 16mm earthing conductor as they fit a 100amp fuse.Maybe it would be good to know why the 25mm is specified, if we understood that we might understand why the c2 is in the book.
The iet do have a phone number. If they can't give a straight answer I might think they are talking sh*t but if you don't ask you won't know
It’s also an eicr zs should take place,leaving all Main bonding connected,how are you suppose to get the pfc & ze measured @ originZs test is a live test. It also includes parallel paths which might be removed. There can be parallel which shouldn't be removed and there's a procedure for managing them.
Live tests are discouraged for obvious reasons as should be taking Zs values that include paths that may be removed.
In that case the c2 seems wrong.Dno on our new build sites stipulate 25mm conductors with a 16mm earthing conductor as they fit a 100amp fuse.