Live working and live testing are two different things.
Also in my opinion (and we can all have them as Inspectors)....
Calculating Ze + R1 + R2 to give you recorded Zs value is not satisfactory and should only be used during initial verification of new install or changes to a circuit to give you a predicted value of Zs which you then confirm by measurement. By doing both tests, you also can highlight parallel earth paths just for you own sanity. Yes, sometimes Zs will be considerably less than Ze + R1 + R2, so what, if you understand parallel paths. When you do and R1 + R2 test you are making temporary changes to install (a link) and after it is put back it should be confirmed by a measured Zs. If only an R1 + R2 test is carried out then added to Ze and recorded as Zs, this creates the possible scenario that an installation gets left less safe following a EICR than when it started if a cpc was to be broken and not noticed.
Zs only is perfectly suitable for EICR as the system has already been commissioned and is operating.