Just imagine the PIR as a switch (with a neutral), permanent live in, SW live out but the PIR does the switching on detection instead of a manual switch
This doesn't sound rightI get all the rest of it but not this bit. The actual klik rose box (not the klik plug) is wired with an L from the DB which is permanently live, so how does the PIR only make it live when it's activated?
We've got 1, 2, 3 and E. 1 and 3 are live, 2 is neutral.
1 always goes in L from the DB but 3 goes in Loop if it's a normal light and A if it's emergency.
I understand how the wiring goes i just don't understand how the PIR works.
Sorry i meant the wire that goes in L on the klik is live all the time but it goes through a bank of emergency key switches next to the DB which are on all the time so it's essentially it's a permanent live.This doesn't sound right
Feed L from DB should go in A for emergency klik or Loop for a normal
You can wire the other way around as long as the plugs are also wired the same but you say other kliks are right
Nah there isn't one these are individual kliks.When you say live all the time at the Klix is this the marshalling box where all the plugs are.
Yeah they all work.If that is the case then either you are mistaken or it is wired incorrectly or intentionally changed to always be on
It should go from MCB to keyswitch to Loop in standard klik or A in emergency
Your extra cable at the keyswitches is not required but probably a conversion from Switch / Keyswitch to Keyswitch / PIR which might have been done wrong
Maybe a stupid question but do the PIRs work? Have you seen them switching?