Take a picture of your CU and MCB and post it on here.
Along with the Make and Model if you have that
I ain't home just now mate, I will be able to post it up in about 45mins.
Teddy
Take a picture of your CU and MCB and post it on here.
Along with the Make and Model if you have that
My advice as a time served spark would be get a girlfriend who only showers for 5 mins
1st thing
Find a 50A Wylex MCB (by looking on Google) or local Electrical Dealer
and Try that
MK, Newlec, etc wont fit!
Thats how they make their money! - they keep making you go back to them to get more parts (MCBs in this case) for their Equipment (CU in this Case).
Don't be fitting a 50A MCB for 6MM Cable!1st thing
Find a 50A Wylex MCB (by looking on Google) or local Electrical Dealer
and Try that
MK, Newlec, etc wont fit!
Thats how they make their money! - they keep making you go back to them to get more parts (MCBs in this case) for their Equipment (CU in this Case).
It depends where the cable is:
If you clip it directly to the wall (not in conduit) it has a higher A rating - its down to how much heat it can disperse.
Sorry got the wrong size MCB - forgot there was a 40A MCB - woops
Straight from the IEE On site guide:
A 6mm cable can take upto:
34A (if enclosed in conduit in a wall)
38A (if enclosed in conduit on top of plaster)
47A (if clipped onto the wall/in the wall with air circulating it)
51A (on a cable tray)