Just a note for Teddy54.... Your original Opening Post left out alot of vital info which we had to virtually squeeze out of you.... The change of shower-
The shower rating-
Cable size etc etc would have got you a quicker result and stopped alot of us running round in circles, and as for been a 3rd yr apprentice you should have been able to work out the showers full running current and realised the clamp meter dis-agreed and also been able to cross reference the time/current tables in the regs, this is all recent learning for you.

I can only hope and assume the situation as stated was new to you and you let your nerves overtake your learning which is easily done until you build you confidence in your abililites, try to approach a problem by getting all the info' thats available, calculating the correct load in this case, then use a clamp ammeter to confirm which in this case gave a suspicious result, so judging by the rating of the shower and its agreement to tripping a mcb within 10-15mins as shown in the time/current tables - i could probably guess that you clamp-meter needs calibration but easy to check on known load like 2kw bar fire etc or kettle....
 
1st thing

Find a 50A Wylex MCB (by looking on Google) or local Electrical Dealer

and Try that

MK, Newlec, etc wont fit!

Thats how they make their money! - they keep making you go back to them to get more parts (MCBs in this case) for their Equipment (CU in this Case).
 
1st thing

Find a 50A Wylex MCB (by looking on Google) or local Electrical Dealer

and Try that

MK, Newlec, etc wont fit!

Thats how they make their money! - they keep making you go back to them to get more parts (MCBs in this case) for their Equipment (CU in this Case).



Really 6mm twe 50 amp breaker , installation method ??? if its 100 then the cable is only rated at 34 amps !! the only way to rectify the problem safely would be to increase the cable size to 10mm and install a breaker at 40 amps
 
1st thing

Find a 50A Wylex MCB (by looking on Google) or local Electrical Dealer

and Try that

MK, Newlec, etc wont fit!

Thats how they make their money! - they keep making you go back to them to get more parts (MCBs in this case) for their Equipment (CU in this Case).
Don't be fitting a 50A MCB for 6MM Cable!

And if this MCB is changed, who is doing the EIC for it? I'm pretty sure that would fall under the scope of notifiable work under Part P.
 
It depends where the cable is:
If you clip it directly to the wall (not in conduit) it has a higher A rating - its down to how much heat it can disperse.

Sorry got the wrong size MCB - forgot there was a 40A MCB - woops

Straight from the IEE On site guide:
A 6mm cable can take upto:
34A (if enclosed in conduit in a wall)
38A (if enclosed in conduit on top of plaster)
47A (if clipped onto the wall/in the wall with air circulating it)
51A (on a cable tray)
 
It depends where the cable is:
If you clip it directly to the wall (not in conduit) it has a higher A rating - its down to how much heat it can disperse.

Sorry got the wrong size MCB - forgot there was a 40A MCB - woops

Straight from the IEE On site guide:
A 6mm cable can take upto:
34A (if enclosed in conduit in a wall)
38A (if enclosed in conduit on top of plaster)
47A (if clipped onto the wall/in the wall with air circulating it)
51A (on a cable tray)

So is a 40A mcb what iam after?
 