Teddy54

Hi folks , I need to change and MCB in my flat as the rating is to low for the circuit its supplying, Only problem is I have never seen this kind of busbar before. Its goes were the Breaker is sat on top of the busbar just behind the screw/clamp and not actually in the seperate bit at the back on the bottom side.

Now my questions is , am I ok to buy a normal breaker and just cut out the pop outs at either side of the screw and sit the breaker on this way?

Hope this makes sense and any help greatly appreciated.
Cheers
 
No. What make is the breaker? Photo? There is no such thing as a "normal" breaker - they're all normal for their make but not necessarily interchangeable. If the breaker keeps tripping there's a reason for it, and simply upping the size of the breaker is liable to cause you more trouble. Get someone in to analyse why it's tripping and give proper advice on the way forward.

PJ
 
There is usually a reason also that the installed size was used. It could be that a reduction on conductor size somewhere on that circuit so was reduced for that purpose.
 
I have tested the situation, When I use my amp meter the shower circuit is giving 36amps and its only a 32 amp breaker. So i was going to replace it with a 40 amp breaker.

The board + breakers are all wylex but having real difficulty finding the exact same breaker, so was wondering if another wylex breaker would be compatable if I cut out the pop outs at the side at bottom on both sides of the breaker
 
I have tested the situation, When I use my amp meter the shower circuit is giving 36amps and its only a 32 amp breaker. So i was going to replace it with a 40 amp breaker.The board + breakers are all wylex but having real difficulty finding the exact same breaker, so was wondering if another wylex breaker would be compatable if I cut out the pop outs at the side at bottom on both sides of the breaker
Don't mess with any breaker. You will find one that will fit in the board - even if it means playing around with the busbar. If its on a 32amp I'd check the size of cable aswell.
 
The question is if you are using 36A - what have you got on that circuit

Most cookers and showers only use 32A Max!

Look at what is drawing that amount of current before anything.
 
Don't mess with any breaker. You will find one that will fit in the board - even if it means playing around with the busbar. If its on a 32amp I'd check the size of cable aswell.

Its wired in 6mm cable. The Breaker Lamb has sent link up for looks like the one.
 
I go back to my post, check how long it would take your existing mcb to trip when pulling your 36 amps
 