a 32A type B will not trip at 36A. you've either got a faulty MCB, or the fault is elsewhere. if the shower cable is 6mm and covered in insulation, upping the rating of the MCB may well result in a 999 call.
 
so, it's either faulty, or the current exceeds 36A. if the MCB is OK< then it would need 50A approx. to trip in 15mins
 
Ok go back to the start - turn shower off and does it trip within 15 mins
If not:
Turn shower on and see how long it takes to trip - a shower should not trip at 32A unless you have a shower with several pumps all drawing the current.

Then see how long that takes to Trip.
 
Quick question:
How long has the shower been installed for?
How long has the 32A MCB been installed for?
How long has the tripping at 32A been going on for?

Answer those questions to give us an idea if its a fault or not
 
Ok go back to the start - turn shower off and does it trip within 15 mins
If not:
Turn shower on and see how long it takes to trip - a shower should not trip at 32A unless you have a shower with several pumps all drawing the current.

Then see how long that takes to Trip.

Its once the shower is on it takes roughly 15 mins to trip. Never happens for me when I shower just for my girlfriend as she takes ages washing her hair etc
 
simple then. set the shower on cold. soon get her out.
 
How long do you take in the shower?

and when your GF gets out is the shower box soaking wet?

Also answer the questions above
 
Quick question:
How long has the shower been installed for?
How long has the 32A MCB been installed for?
How long has the tripping at 32A been going on for?

Answer those questions to give us an idea if its a fault or not

Its a new shower. It happend with the old shower a few times then eventually that shower chucked it. I
MCB about 10+ years.
A few months.
 