what's the kW rating of the new shower?
 
Can I ask are you a sparky or a DIYer?

Not a problem either way - just so we know what Level to talk to.


Its sounding like a fault, no shower should trip at 32A at all.

If you upgrade it, you will have bigger problems as already said.
 
Can I ask are you a sparky or a DIYer?

Not a problem either way - just so we know what Level to talk to.


Its sounding like a fault, no shower should trip at 32A at all.

If you upgrade it, you will have bigger problems as already said.

Iam a 3rd apprentice. Not done alot of house bashing though which is why Iam a bit puzzled.
 
The circuit breaker is there to protect the cabling. What size is your shower? Has it been upgraded without the cable being upgraded accordingly?

PJ
 
am I right in saying Power Formula

P=VI
=32x230
=7360
=7.3KW Shower

Is this what you have Teddy?
 
yes was just going to say that a1guvner..... how many hours are they in the shower for???? as the info you've supplied wouldnt have tripping issues unless their is other cable, shower, install method issues.
 
Back to get a proper fitting mcb, dont refabricate its housing to suit your install, you have waited this long with it tripping a little bit of time finding a proper fitting breaker
 
Teddy

Take a picture of your CU and MCB and post it on here.
Along with the Make and Model if you have that
 
Back to get a proper fitting mcb, dont refabricate its housing to suit your install, you have waited this long with it tripping a little bit of time finding a proper fitting breaker

Yes i know, was just a bit of daft thinking earlier on as had never been in the situation before.
 