Your 1.8kW/phase is about 8A, so 10A or more OCPD should be fine, subject to inrush limits.
If you control inrush then the 10A B-curve MCB is OK and it needs cable below 3.42 mOhm/m so all examples except 16mm 4C are fine.
If you used a 16A B-MCB for more inrush tolerance then it is 2.15 mOhm/m, so either 25mm 4-core and a supplementary 16mm earth, or 25mm 5-core is needed, etc.
If you control inrush then the 10A B-curve MCB is OK and it needs cable below 3.42 mOhm/m so all examples except 16mm 4C are fine.
If you used a 16A B-MCB for more inrush tolerance then it is 2.15 mOhm/m, so either 25mm 4-core and a supplementary 16mm earth, or 25mm 5-core is needed, etc.