If device fails it trip only one protected circuit, not all circuit will be off in RCD unit
So is this a high integrity unit then?
If device fails it trip only one protected circuit, not all circuit will be off in RCD unit
YesSo is this a high integrity unit then?
BG?
The only maximum rating for a MCB is either the:Also advice me please with mcb sizes if i am correct about radials. As far as i rememmber from regs maximum mcb rating for radial is 16amp.
Can you connect each switch to radial? i mean run dedicated supply to each switch?So on a typical RFC you can link the supplies to each switch in the loop. But again needs a bit of care.
Thank you! So if i run 2.5mm radial from rcbo 20A to one switch,labeled as washing machine then run another 2.5mm radial from another RCBO 20a to another switch labelled dish washer. WIll that be good practice?You can use them as any normal switch, so if you want each on a radial feel free to do so.
Yes, that is perfectly good practice.Thank you! So if i run 2.5mm radial from rcbo 20A to one switch,labeled as washing machine then run another 2.5mm radial from another RCBO 20a to another switch labelled dish washer. WIll that be good practice?