Been doing some refurb work for someone. He paid National Grid £1700 odd to move his gas meter from the hall cupboard he wants to use as a toilet. This old bit of barrel's now redundant.

Let's play spot the missing gas bond shall we?
 
Did a re-wire a while back where the kitchen fitter removed the bonding across the boiler pipes as he could not gets the tiles to fit otherwise.

Regards wa
 
I suppose you could through crimp the bonding conductor and follow the gas pipe to its new position, unless there is an easier route.

I wouldn't worry about Gas fitters removing protective bonding conductors, unless they install a new boiler and then they usually demand payment for upgrading.

Very sloppy.... "Not my job mate !"
 
Last edited:
Did they use plastic pipe for the new gas connection?

If so then it's not an extraneous conductive part and wouldn't usually need bonding.
 
The pipe in the picture looks like metal to me.
As such it would appear to be an extraneous-conductive-part and requires bonding.
Good job they left the old bonding conductor.
 
As this appears to be an incoming pipe why would it be bonded all bonding goes to the consumers side of the meter and there isn't a meter connected or any consumers pipework in the picture
 
The fact that there is no meter, doesn't stop the pipe from being extraneous, nor does it abrogate the requirement to provide protective bonding.
 
Pipe is the disconnected remains of the incoming gas before they moved meter to an external jewson box. That bit of 10mm was the existing bond from before I started working there. It HAD been connected to the consumer's outgoing pipework and until National Grid moved the meter was perfectly happy doing its bonding business.
Went back this evening and customer's not heard a peep out of N. G.
Builder's removed that bit of barrel now.
 
Last edited by a moderator: