Hello

New build commercial property with a 90KVA incoming supply, 125A fuses in the service head.

What size isolator would you all fit on top of this to feed a TP distribution board?

125A switch fused isolator with 125A fuses? 125 isolator, 100fuses? 100 isolator with 100fuses?

Isolator with even smaller fuses for selectivity?

Opinions please?
 
Is this a trick question?

For a 125A supply a 125A (or bigger) main switch would be required.

And if the DB is any distance from the supply then a switchfuse will be required.

Unless of course there are any other requirements from the DNO.
 
Is this a trick question?

For a 125A supply a 125A (or bigger) main switch would be required.

And if the DB is any distance from the supply then a switchfuse will be required.

Unless of course there are any other requirements from the DNO.
Hello

No, only asking what size switch fused isolator you’d install.

Meter fitters have requested an isolator installed on top of the service head with tails down into the head.

Wondering what size switched fuse you’d install and if you’d downgrade the fuses or not
 
Are you considering overcurrent, short circuit current or both to achieve coordination?
What is the maximum demand of the installation as you need to know this.
Does the isolator actually need to be fused?
If the fuses in the head and isolator are of the same type you can usually apply a factor of 1.6 so 125A ÷ 1.6 = 78.125A for your isolator fuse size.
 
Max demand is definitely over 78 amps per phase so it’s just not feasible to downgrade the fuses to 60A or even 80A

This is a newly installed supply requested by the customer.
 
Hello

No, only asking what size switch fused isolator you’d install.

Meter fitters have requested an isolator installed on top of the service head with tails down into the head.

Wondering what size switched fuse you’d install and if you’d downgrade the fuses or not

If they've requested an isolator the that's what I'd install, an isolator rated at the full supply capacity.

Why would you want to reduce the capacity of the supply after someone has gone to the trouble of specifying and paying for a 125A supply to be installed.
 
I was and have always been under the impression that you need to downgrade for selectivity. Too ensure the fuses blow at the isolator rather than the cut out should they ever need to

Is this not the case?
 
I was and have always been under the impression that you need to downgrade for selectivity. Too ensure the fuses blow at the isolator rather than the cut out should they ever need to

Is this not the case?

This leads to another question, why do you want to fit a switchfuse instead of a switch as the main switch? Has this been specified by someone? is there a distance of greater than 3m to the first DB?

Yes you need to consider selectivity, but you also need to consider that someone has specified and paid a lot of money to have a 125A supply installed so they are going to be somewhat unimpressed when you restrict them to 80A.

You also need to consider what would or could happen to cause those 125A fuses to rupture. If you've designed the rest of the installation correctly, with due regard to selectivity, then they will only rupture if something quite catastrophic happens.
 