Only ever had the chance to use it on one job. Six sub boards in an office block. After being used to nothing but SWA I fell in love with the stuff, so easy to work with.
 
Are you suggesting that the insulation on the neutral conductor is not satisfactory?

Not at all , i find pvc split con great to work with , but it was originally developed for use with DNO supplies which work to different regulations , not domestic installations.
Therefore a bit of thought is needed before using it.
Plus the fact that it may need rcd protection whereas swa does not limits its uses somewhat.
 
Depending on the size of split concentric cables, i bet the majority of the final terminations look like a pig's ear of a job!! There is to my view, only one means of terminating these cables that will make them look anywhere near decent, and i doubt very much if that method is used in even 1% of this type cable terminations... lol!!
 
Last edited by a moderator:
If you have any pride in your work then it needn’t look a “pigs ear”. I could take exception to your comment, but I won’t.
 
If you have any pride in your work then it needn't look a “pigs ear”. I could take exception to your comment, but I won’t.

Not sure why you would take exception to my comment, as you could probably do a more than decent job using amalgamating tape, as well as with a 3 leg heat shrink breakout.

But in all honesty, how many of these new electricians could?? Come to that how many would even try!! lol!!!
 
I used heat shrink tubing but couldn’t get the correct boots so used a larger tube to shrink over the crutch area.
It made a nice change to not be working to M&Q.
 
How do you terminate these split concentric sub-main cables??

Using a 3 way cable breakout. It slips over the end of the split concentric, separates the conductors and then heat shrinks down. It's got a glue inside that melts once heated and makes a very permanent termination.
It looks neat, but nowhere near as neat as an swa gland.

edit:
Hmm I was far too slow here, didn't notice there was a second page. Oops!
 
Last edited by a moderator:
you can do a decent job with some small tie wraps, a lot of the new build housing i was working on was done with it for the sub mains.
 
Are you suggesting that the insulation on the neutral conductor is not satisfactory?

Like every wiring system, there are applications where specific cables can be used. I see no reason why split concentric cable cannot be used by non-DNO for sub mains installations. It is never suggested that it is an armoured cable and should not be treated as such.

I personally use it for the majority of domestic sub-main installations, where appropriate. The reason I do is because I find it much more flexible and therfore easier to work with than SWA.

100% agree and do exactly the same.

Brilliant stuff.
 
it was and might still be popular on street lighting installs where if doing 2 or 3 into an SMK cutout you have no opotion but to make your ends off as neat as possibl epersonaly id use pvc tape due to space and never getting heat shrink The training we got used loose fitting sleeving on the N E cores making for a pish looking job
 