hi guys
ive read somewere the mounting distance for saddles when using conduit, ie how far apart they should be, cant find it anywere
any idears?
cheers
The spacing for 16<=dmm conduit is: 0.75m horizontal and 1.0m vertical for rigid metal
0.75m horizontal and 1.0m vertical for rigid insulating
0.3m horizontal and 0.5m vertical for pliable
The spacing for 16<d>=25mm conduit is: 1.75m horizontal and 2.0m vertical for rigid metal
1.5m horizontal and 1.75m vertical for rigid insulating
0.4m horizontal and 0.6m vertical for pliable
The spacing for 25<d>=40mm conduit is: 2.0m horizontal and 2.25m vertical for rigid metal
1.75m horizontal and 2.0m vertical for rigid insulating
0.6m horizontal and 0.8m vertical for pliable
The spacing for >40mm conduit is: 2.25m horizontal and 2.5m vertical for rigid metal
2.0m horizontal and 2.0m vertical for rigid insulating
0.8m horizontal and 1.0m vertical for pliable
Taken from OSG page 115 table 4C.