ive got chocky blocks in db's with pfc of 20k.people are missing the point of the question which is do connector blocks have or/are tested to any withstand any fault current?
 
Yes, and very likely you also have bits of cable in said DB that are tiny skinny little things and are not capable if taking 24kA (note capitals!). Are you saying these cables have no place there?
 
As people above have already said, the PFC is more to do with the breaking capacity of the protective device and as connectors don't make and break circuits then they wont have a rating.

When an MCB Fuse or any circuit protective device breaks an arc develops. The breaking capacity (normally in kA) is there to tell us that the device under fault conditions is capable of containing this arc.
 
this stems from a electrical insurance inspection by royal and sun aliance where the inspector has said all connector blocks should be removed as they would not survive any potential fault currents
 
this stems from a electrical insurance inspection by royal and sun aliance where the inspector has said all connector blocks should be removed as they would not survive any potential fault currents

It may be worth finding out if you can where the person who wrote the report has got his information from.
 