Yep you can but if there is a RCBO on it the Rn will be higher than R1 true or false
Pict

I nominate this post for the most stupid of the week. it's only monday though, so plenty of time to do better.
 
if you are doing a continuity test at a socket, then the cable is dissed from the CU and shorted out. L-E for R1+R2, etc. so the \RCBO is irrelevant.
 
Well if you short it in the RCBO then No :p

Never tried it or seen it tried so dont know but My guess would be that there would be no difference as it should still take the path of least resistance.

But why such a random question??
 
You could leave the live in the outgoing term and add the cpc for testing purposes but obviously with the board isolated and the rcbo off.
Still don't get your point.
 
I was replaceing a couple of cracked sockets in a hotel bedroom RFC circuit and as it was a busy lunch time and the board being in a place that restricted access to the kitchen I opted to test at a socket R1 0.19 R2 .31 Rn .89, went round all other sockets no faults , I waited around, had a pint and a ploughmans FOC as well after the buzz I did the Cont Ir auto tested the RCBO all at the board and the readings were ok, w,ent back to the original socket and got the same Rn and I have been scratching my head since why the anomaly at the socket
Pict
 