eskimo39

Hi I was working Xmas eve at a friends house installing some decorative faceplates to all his sockets. I turned off the power at the MCB and then when I checked accross Phase and Neutral to determine that the supply was off, got a continuity beep from my Fluke T5.

I checked this on all the downstairs sockets and got the same result. However on the upstairs sockets It showed no continuity and no voltage. Can anyone explain why??

Cheers
 
If appliances were still plugged in on that circuit you would get continuity through the line conductor, through the appliance and then back through the neutral conductor. You will also get continuity between line & earth if the neutral is still connected at the distribution board.
 
Last edited:
Sounds obvious now!!!!! :eek:

I will check again when I next go down and unplug all appliences before commencing a test again.

Thanks ever so much.
 

Reply to Continuity Between P & N in the Australia area at ElectriciansForums.net

Similar Threads

I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
718
I saw a Fluke 1653B on Gumtree local to me being sold as faulty. Fault was stated as no continuity between 'N' and 'PE' ports on the resistance...
Replies
3
Views
432
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
259
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock