mate....you need to think a little before posting this kind of thing...Prepare to upset your client by telling them it needs a new feed, disturbing all that lovely new plaster!
Had this done to me a couple of times, why do people not make decisions at the right time??!
He is.![]()
like it. dual outlet box with cooker connection unit one side and a socket of FCU on the other. no disruption then. all below worktop.
will need 13A fuse either in plug top or FCU for the oven.
Surly you would be alright on a 32 after applying diversity -10 amps then -30% depends on the client tho that's just a general guide
Just fitted one of these last week and must say they are good and sturdy and easy to fit!Don't need all that, just one of these and the job's Done!!
Click 45a Easyfit Dual Appliance Cooker Outlet Plate
Im from ryton, not far away
doing kitchen upgrade oven was already wired in 10mm all ok new oven and micro oven wired off switch giving me 6100watt with out diversty problem being oven and micro oven pre wired in 1.5 flex. flex cannot be replaced will this be compliant on a 32amp mcb as it was wired when i came to fit two seprate loads from one cooker switch one to micro oven one to main oven would this be ok as it would only be pulling load of the micro oven through that flex and not pulling the load off oven not pulinng the load off both through flex if both on. flex lenght less than three meters. will be nite mare to run new circuit for micro oven i know two oven meant to be on two switches everything plastered and painted.