was thinking about that but but one oven is 3500 watt which would give over 13 amp and micro oven states that 15 amp supply required trying to make best out off bad situation may go with 13amp fcus but dont want them to blow behind cookers once in place i dont know why the manufacturers dont up rate the flex to suit power demand because it pretty much on the limit was going to just up rate the flex as this cant be done may have to fit fcu or lower the mcb to 20 amps which could cause to trip even after diversty is applied but this mite be better than fuses blowing behind aplliances
The posh end up the hill or the slightly rougher end Ross Ave, Lister Ave and those blocks of flats?He is.![]()
manufacturers instructions state that each oven needs a supply of its own at 15amps or above but as this is allready wired in and didnt know about oven specifications they want me to connect both just looking for a solution to this problem that doesnt require putting a new feed in ,you can have a hob and oven of same switch but two ovens of similar wattage in same wall unit meant to be on different switches apparently kind of like double oven one oven on top of the other running another feed not really practical.
I almost bought a house there from a mate I once had.
if you have a 6mm feed on a 32A breaker, then fit each with a 20A D/P switch. they are classed as fixed loads, so the 32A will provide short circuit protection. overload is considered to be unlikely on a fixed load. 433.3.1 (ii)
Don't need all that, just one of these and the job's Done!!
Click 45a Easyfit Dual Appliance Cooker Outlet Plate
How you fusing the hob down.
How you fusing the hob down.