If it came with a 1.5mm cable then you shouldn't start changing cable without talking to the supplier. I would do as someone else stated just put a 13A plug on.

I'm pretty sure you can't use the grill and oven at same time so the max for that section of oven would be 2kw. What are the ratings of the hot plates or for that matter the total rating if the oven stated on the plate?
Thats bad advice, the 1.5mm2 cable is a tri-rated cable and if there is no plug top on it then it is probably because a 20 amp supply is recommended by the manufacturer. Never add a plug to a new appliance if it does not come with one fitted, very bad mistake.
 
The other thing to mention is surely there is a load label on the cooker or in the Bloody manual, all this guess work regarding Appliances is just plain daft.
 
If it came with a 1.5mm cable then you shouldn't start changing cable without talking to the supplier. I would do as someone else stated just put a 13A plug on.

I'm pretty sure you can't use the grill and oven at same time so the max for that section of oven would be 2kw. What are the ratings of the hot plates or for that matter the total rating if the oven stated on the plate?


Hi Scornio

I always thought this, until recently (!), proudly announced the said fact to the lady owner of her 5k range cooker to which she replied


"You can on this one"

it was a huge great range, that came with its own 10mm2 3 core cable attached (as serious a cable as I have ever seen on a domestic cooker), and a crafty little setting: "Pizza"

....which lets you grill and use the oven at the same time!!!
 
If there is a plug fitted, plug it in.

If its a cable that needs terminating. YOU need to read the installation instructions, but I suspect a 20A could be in the information supplied.
 
Tri-rated cable is designed to run at a higher temperature than standard PVC flex, and should only be used at that rating when connected to switchgear also designed to run at high temperature. We have the same issue when using XLPE swa...just because the cable can run hotter, it doesn't mean that it should.
 
I wouldn't say it was bad advise. Do we even know that it's trirated flex??! And why would it make any difference to the disconnection of the 13a fuse? It can carry a higher temperature?!
I bet that the total power consumption for this cooker is no more than 2 kW that's why the flex is selected accordingly.
 
Well by my working applying diversity it requires 19A
 
Last edited by a moderator:
Easy install comes complete with 1.5m Cable. copied from spec. that's a 5 ft. length of cable.
 
Might be missing a trick but can't see anything about a 1.5 flex in the spec, it does say supplied with 1.5 metre cable
 