I am rewiring a house I recently bought and have a couple of questions;

I have a lead water pipe coming into the kitchen and it is not bonded back to the MET. The supply looks like an old 16mm2 cable. I take it a 10mm2 earth is sufficient. Is there any requirement to bond anything else in the property?

I have an oven and hob to wire in also. The oven is a single oven 2.2kW (9.6A) and the hob is a 27A ceramic hob, the manufacturers documents state it should be connected with 2.5mm2 cable, this seems too small to me.

I was thinking of doing the following;

Installing a 16A radial in 2.5mm T&E for the oven with a 13 A FCU.
Installing a 32A radial on 4mm T&E for the hob with a 45A DP switch.

Can either of the switches be mounted inside cupboards or do they have to be above the work surface for access?

By the way, the cables will run under a wooden suspended floor (floorboards).
 
what's the earthing arrangement? if it's pme, 10mm bonding cable is required. if TN-S you could probably use smaller, but fit 10mm anyway.

your cooker arrangement looks good. although a single 32A circuit using 6.0mm to a 45A switch, then a split outlet, direct outlet for hob, FCU for oven, on one of these would be more cost effective.
1570615991418.png
advantage being you can have 1 outlet as FCU or a single socket, depending on whether the oven comes with a fitted plug (top).
switches/isolators can be in cupboards as long as securely fixed and readily accessible.
 
what's the earthing arrangement? if it's pme, 10mm bonding cable is required. if TN-S you could probably use smaller, but fit 10mm anyway.

your cooker arrangement looks good. although a single 32A circuit using 6.0mm to a 45A switch, then a split outlet, direct outlet for hob, FCU for oven, on one of these would be more cost effective.
View attachment 52983
advantage being you can have 1 outlet as FCU or a single socket, depending on whether the oven comes with a fitted plug (top).
switches/isolators can be in cupboards as long as securely fixed and readily accessible.
Thanks for the info above, I think its TNS, i'll have a look later but will go with 10mm to be safe as you say.

The reason for my cooker wiring plan is that I have all the cables and fittings to do the job without having to buy anything else.
 

Reply to Cooker question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
590
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
593
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
779
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
663
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock