Agreed as all above. Every install different,sum cases 10mm sum 6mm and weigh up the cennario,but never below! 4mm? Only if its a very poor granny who we don't want to take money off! Lol.. Case closed :)

4mm would be good for the granny maybe................but

If I had just bought her house when she 'moved on' lol..........I would hope the spark had put in 10mm for future expansion( new range or whatever) then that would save me loads of grief if it was a shhht run for the cable.

Just out of curiosity,as I'm not a domestic spark,............whats the difference, price wise, for 20 metres of 4/6 mm compared with 20 metres 10 mm ?
 
4,6,10mm is £42,60,105 for 50m on one site. plus vat I think.

I didn't post because of cost - just pointing out the regs.
 
Obviously the installation conditions have to be considered.

However, using 6mm² on a 32A mcb is a throw-back to 30A 3036 fuses where 4mm² (max 37A) is not suitable because of the 0.725 derating factor (30 / 0.725 = 41.4A)
(I can't remember who pointed this out - I hadn't thought about it, you just get used to things.)

Assuming method C and no integral socket at switch and using diversity.

So -
4mm² 32A mcb good for 20kW (hence the 15kW quoted because of integral socket)
6mm² 45A mcb good for 30kW
10mm² 50A mcb good for 34.4kW

That's what the rules say.

I suppose you could have a 63A on the 10mm² if necessary.

The 0.725 de-rating factor is relatively new, (around the late 60's or early 70's i think) whereas the old 7/044 30A 3036 has been around far longer, as has the cooker diversity formula...
 
4,6,10mm is £42,60,105 for 50m on one site. plus vat I think.

I didn't post because of cost - just pointing out the regs.

I was just curious Geoff............I don't pay for my gear so it's easy for me to spout on here.
Would be different if I was paying for it lol
 