It's not unreasonable Kate, it's just abit OTT and will cost more.
Not if the cable has a long run and goes through the loft

It's not unreasonable Kate, it's just abit OTT and will cost more.


dave, your spellings atrocious. have another beer.

Not if the cable has a long run and goes through the loft![]()
Oooh. Yea I get ya. Think it's cause my customers don't question me. I was hired to connect up a new cooker some time last year...went to do it, had a horrible job of explaining that their swanky new double range cooker they just bought can't be connected to the old ****ty 4mm. Have a feeling they just did it themselves when I left!!
)Well yes, but that depends on the installation itself, and the installer himself will then decide if to up it to 10mm. Most cookers will be fine on a 6mm, some even adequate on 4mm.
Absolutly in agreement with thisAlways cut your cable long..................
Always 'oversize' your cables....................
Do the calcs then add a bit on for future reference.
Easy to downgrade but fkin hard to upgrade without hassle)
For the sake of a few quid l
I hear what your saying but everyone is saying 6mm is ok on 32A breaker for up to 15kw cooker circuit.............Is it?
6mm run 30/40 metres through the loft under insulation on a 15 kw load............shower or cooker?
Is that acceptable............can't be arsed to work it out lol
Every install is different surely and must be treat that way?
Sorry for delay in answering, see post 52Why 40A? Just interested. Daz
my answer is on post 52Why?
Cookers up to 15kw are adequate on a 30A/32A.
my answer is on post 52