Oooh. Yea I get ya. Think it's cause my customers don't question me. I was hired to connect up a new cooker some time last year...went to do it, had a horrible job of explaining that their swanky new double range cooker they just bought can't be connected to the old ****ty 4mm. Have a feeling they just did it themselves when I left!!
 
Not if the cable has a long run and goes through the loft:)

Well yes, but that depends on the installation itself, and the installer himself will then decide if to up it to 10mm. Most cookers will be fine on a 6mm, some even adequate on 4mm.
 
Oooh. Yea I get ya. Think it's cause my customers don't question me. I was hired to connect up a new cooker some time last year...went to do it, had a horrible job of explaining that their swanky new double range cooker they just bought can't be connected to the old ****ty 4mm. Have a feeling they just did it themselves when I left!!

Always cut your cable long..................
Always 'oversize' your cables....................

Do the calcs then add a bit on for future reference.
Easy to downgrade but fkin hard to upgrade without hassle:))

For the sake of a few quid ffs lol
 
I always allow a bit either way, not everyone just uses a couple of rings and the oven for a short time or on low settings. Re 10mm that is in my opinion correct rating of cable for cooker specified. Re cost, its not that much extra over a few metres in length, Re 40 , i consider it safe. I use separate circuits in kitchens for appliances and sockets and cooker. I also look at how many bedrooms house/flat has. If 3/4 bedroom its likely to be a family home kids etc, ie more use of kitchen appliances etc. Some people may consider me to be over the top, but i feel it is the correct way. PS I've just put my tin hat on.
 
Well yes, but that depends on the installation itself, and the installer himself will then decide if to up it to 10mm. Most cookers will be fine on a 6mm, some even adequate on 4mm.

I hear what your saying but everyone is saying 6mm is ok on 32A breaker for up to 15kw cooker circuit.............Is it?

6mm run 30/40 metres through the loft under insulation on a 15 kw load............shower or cooker?
Is that acceptable............can't be arsed to work it out lol

Every install is different surely and must be treat that way?
 
Always cut your cable long..................
Always 'oversize' your cables....................

Do the calcs then add a bit on for future reference.
Easy to downgrade but fkin hard to upgrade without hassle:))

For the sake of a few quid l
Absolutly in agreement with this
 
I hear what your saying but everyone is saying 6mm is ok on 32A breaker for up to 15kw cooker circuit.............Is it?

6mm run 30/40 metres through the loft under insulation on a 15 kw load............shower or cooker?
Is that acceptable............can't be arsed to work it out lol

Every install is different surely and must be treat that way?

I agree, you need to take into consideration the paticulars of the job and in some cases it won't be. You as the installer have to decide/rate on site what you feel is suitable and acceptable :)

I understand though, maybe it is to hasty to say 6mm for up to 15kW. It's just in general that it's accepted, any electrician will be able to tell (hopefully) whether its not though lol.
 
Agreed as all above. Every install different,sum cases 10mm sum 6mm and weigh up the cennario,but never below! 4mm? Only if its a very poor granny who we don't want to take money off! Lol.. Case closed :)
 
Obviously the installation conditions have to be considered.

However, using 6mm² on a 32A mcb is a throw-back to 30A 3036 fuses where 4mm² (max 37A) is not suitable because of the 0.725 derating factor (30 / 0.725 = 41.4A)
(I can't remember who pointed this out - I hadn't thought about it, you just get used to things.)

Assuming method C and no integral socket at switch and using diversity.

So -
4mm² 32A mcb good for 20kW (hence the 15kW quoted because of integral socket)
6mm² 45A mcb good for 30kW
10mm² 50A mcb good for 34.4kW

That's what the rules say.

I suppose you could have a 63A on the 10mm² if necessary.
 