B
bartkusal
Practical guide to inspection testing and certificating by Christopher kitcher......
This is there exact answer
"Zs will be 0.34+0.6=0.94 ohms
So Zs=0.94 ohms
The maximum Zs for a 30A Bs 3036 fuse from table 41.2 inBS 7671 is given at 1.09 ohms.
Using the rule of thumb for temperature correction the maximum permissible value is : 1.09 x 0.8 = 0.87 ohms
This value means the gained value is acceptable"
Ok, mistake in the book it is, then