why would you not use rcbos on commercial lighting MDJ? we use rcbos all the time for commercial lighting

due to the inconvienience / loss of revenue / potential hazards created by losing lighting in a work area from a rcd thats only tripped in the first place due to accumalative earth leakage from otherwise fault free circuits.
on my current commercial project the only circuits with rcbos are gen. purpose sockets.
everything else rcd free.
 
thanks i only thought things like lots of computers on a circuit cause enough earth leakage to trip rcbos , are light fitting likely to cause this too
 
why would you not use rcbos on commercial lighting MDJ? we use rcbos all the time for commercial lighting

Quite simple, it's an industrial unit.

The workforce is going to be really peed off when the lights go out on a damp humid day and they have to find their way out in the dark.

You or someone in you're company are/is a fool.
 
yeah we must be , but its funny as we never get any nuisance tripping , must just be luck eh
 
yeah we must be , but its funny as we never get any nuisance tripping , must just be luck eh

Me neither on some of mine mate................including welders/compressor and 3 phase boards:)
All tests good for ADS with the added 'bonus' of rcd protection.................maybe we should take them off because they aren't really needed eh !!!!
 
in our case we use rcbos for mostly everthing in the case of the lights , the switches for switching them on are usually metal clad and when u work in warehouses and factorys u will find out people dont turn light switches on with their finger they punch them on kick them on rip them off the wall and although if they get a shock while doing this its there own fault we would prob get the blame in some way so its just as easy to fit an rcbo , and as i said never had any problems with nuisance tripping
 
A warehouse?

I’ve been in foundries and quarries all my working life. Both industries are full of animals (called production workers).

Never had the need to fit E/L protection to the lighting, if they damage a switch the fuse blows. (Followed by me jumping up and down on their neck).

E/L on industrial/commercial lighting is nothing but a con trick for repeated call backs.
 
I think the brain-washing effect is evident here pre 90's nothing really had RCD protection then it was requested for sockets that could be used for outdoor use then now its really covers everything in a domestic situe due to the 50mm rule below the surface. Ironically the death rates from electrical shock hasn't really changed much ....so a century of electrics where we have only started to implement rcd protection and all the newbies can't understand the reality of circuit without E/L protection ...... yes in the wider scope its safer but in the real world if installed correctly it was never a concern ....the rcd protection was only enforced after a MP lost his daughter due to a kitchen fitter running cables on a diagonal and she drilled the wall, had the kitchen fitter followed regs it would never have happened but been an MP he got a change in the regulations.....


I see a culture of sparkies scared to leave RCD protection put when its not required.....
 
yes i suppose you are right darkwood its like using a D type mcb for 3 lights when its not needed :-)
 
That is the difference though to having your arse on the line line when they do trip or it been of little consequence in a less crucial set-up, i have corrected other installs as mentioned earlier due to this and the in house sparkies wouldn't believe me either but its never tripped since (this was an hospital).
Its amazing the swinging power raw calculated data has on 5 electricians all trying to belittle you and your views to their boses, i even put the head of department on the line to tech' at schneider who happily confirmed my point explaining why i was correct which was the point where they decided i was correct lol ;)
 