Hi, hope someone can answer my question.
I have recently installed a new bathroom, the bath is steel, and i have no electrical appliances or points in the bathroom, except for the lights of course.
When i had the old floor up i noticed that one of the water pipes was clamped and a cpc runs downstairs to the cu. Basically do i need to cross bond the pipework for the bathtub and the washbasin..? Thanks for any reply.
 
Try and run the supp bond from the bathroom lighting cpc as well to ensure that everything is buzzing off the same hymn sheet, or maybe change the upstairs lighting mcb for an rcbo. If you've already fitted the bath etc I guess the last thing you want to do is rip up the floor and walls !!
 
Hi mc497, wot your seeing is dating back to the old regs probably 15th edition where supplementary bonding used to have to go back to the CU. If your not gonna RCD protect the lighting circuit, disconnect the wire going back to the CU and cross bond the pipe work, the bath and the cpc in the light to avoid any potential difference in the bathroom and also to stop any earth faults from any other circuits that are going back to the CU from going into the bathroom.
 

Reply to Cross bonding or not..? in the Australia area at ElectriciansForums.net

Similar Threads

Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the...
Replies
25
Views
6K
hi there as i write this i realise i have 3 interconnected questions about fused switches; two relating to my boiler (hope its not to cheeky to...
Replies
3
Views
1K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock