E

Edd

Hi Guys,
Next week I'm fitting four 3 phase check meters, these will be done with CT's. it say in the info that each phase also has a fused down supply to 4 separate terminals L1 L2 L3 and N are these just to supply the meter or do they use this in some way to measure the current.
I ask as i would like to only fit a 3 Phase MCB to supply all 3 meters in Parallel, and hope its just the CT's that measure the current.
Thanks Guys, and girls
 
Thanks for that. my wonder was can i supply all 4 meters from one set of fuses? if they are just used for supplying the meter then I can see no problem, but if they are used insome way to measure the current then i will end up with 12-16 inline fuses!
 
Thanks for that. my wonder was can i supply all 4 meters from one set of fuses? if they are just used for supplying the meter then I can see no problem, but if they are used insome way to measure the current then i will end up with 12-16 inline fuses!

Ed, Normally each CT has it's own single phase MCB, clearly labeled. However in the last couple of years I have seen a number of people put these on 3 phase MCB's and a Neutral Block. The fact is the Neutral can carry a significant amount of energy all by itself in large installations so this should be protected, because it is actually protecting the METER and not the CT. I do not like the 3P+N approach and when this was done recently in our DC new modules we insisted that Prism change this to individual protective devices.
 
The voltage is a reference for the meter to calculate KWHr I*V.

You could put all four meters on one MCB + the neutral connection, I wouldn’t be happy with you if you did. All our meters were individually fused at 2A also a neutral test link fitted. It’s a standard practice for metering.

PS it used to take one of the mates a full day to read all the meters on our section alone.
 
Edd, I should also point out that some of the new meters also require a 230V single phase supply (usually via a 12V Tx) to allow the meter enough power to run network systems for remote monitoring, alarms etc..
 
Unless I’ve totally misread Edd’s OP the meter requires a 3Ph+N reference supply. NOT 12V.

Using current measurement only for metering is possible but not reliable or accurate!
 
Unless I’ve totally misread Edd’s OP the meter requires a 3Ph+N reference supply. NOT 12V.

Using current measurement for metering is possible but not reliable or accurate!

Thats right, As with the above I'm now going to fuse each meter separately, i'm making a box up as I type!

Thanks again
 
Unless I’ve totally misread Edd’s OP the meter requires a 3Ph+N reference supply. NOT 12V.

Using current measurement only for metering is possible but not reliable or accurate!

Tony, you're well behind the curve on technology chap. For a start all 3 Phase meters used internal CT's for metering anyway, but many modern electronic ones, especially check meters, take their power from a reference voltage from the CT, this is also why many newer ones also require a separate 12V/230V/400V supply as this reference voltage is unable to supply power to run the meter services for alarms, network connections, logging etc.


This is not true for all of course, there are many that are designed for direct input of 3P services.

Here is the ones recently installed in the DC.

LINK
 
Tony, you're well behind the curve on technology chap. For a start all 3 Phase meters used internal CT's for metering anyway, but many modern electronic ones, especially check meters, take their power from a reference voltage from the CT, this is also why many newer ones also require a separate 12V/230V/400V supply as this reference voltage is unable to supply power to run the meter services for alarms, network connections, logging etc.


This is not true for all of course, there are many that are designed for direct input of 3P services.

Here is the ones recently installed in the DC.

LINK

I may be behind the times, but I read Edd’s OP!

CTmetering_zpsf0841c6a.jpg
 

Reply to CT meters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, I’m testing some electric meters. As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and...
Replies
3
Views
479
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
506
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
423
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
336
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock