sima24
Thanks for the advice tho guys, i supose putting it on 2 radials would be the best option if i cant locate the fault within his "budget".
Because i would rather connect it back on a ring. If installing as 2 radials is it not going to cause any problems with labelling, and cant see how zs readings would improve
thank god...the voice of sense...Having two radials junctioned at the MCB is within the regs, as long as the OCPD is suitable for the circuit, a 20A MCB has a higher allowed max Zs anyway, you are allowed a theoretical max of 1667 ohms due to the RCD, I don't suggest using an RCD to mitigate a massively high Zs or mask a fault, but as this is only very marginally high, and may be normal for a radial it would mitigate in this instance.
Have a look at App15 in the BGB.
As to you would 'rather have it on a ring', so long as the circuit complies with the regs, then personal preferences don't enter into it, unless you were installing a new circuit, you can only test what is in front of you.
this is it...`global` IR testing of live conductors..to earth...thats a quicky...The thing is R75, you don't even need to do a 'full blown' Eicr, a couple of basic tests at the survey stage can highlight the vast majority of common faults/scenarios, or at least make you aware of what you are letting yourself in for before even quoting for the job, and it only takes a couple of minutes to do on a 'normal' domestic setup with a half a dozen circuits or so.
first port o call is that 68.....get yoursen a Ze....before owt else...you can do stuff about dodgy system...but if the external`s high....its the DNO and the clocks ticking....sometimes for a very long time with them..lol...thats after you`v managed to get through to someone with anything about em..lol...
Too true, a Ze reading is one of the first tests I do