Jun 21, 2009
375
24
93
Cornwall
Can a (eg, MK BS4293 63A 30mA) RCD be used as a main switch in a CU if it's the ONLY source of switching for that CU? I'm about to start work on a CU with RCD-Breaker-Breaker-Breaker-etc-Main Switch-Breaker-Breaker-Breaker-etc.

I obviously need to add a new RCD for the second split but would the board then need a main switch for the whole thing? These boards used to have labels saying something like "All switches must be off to disconnect from the supply".

...wondering...
 
All installations should have a single point of isolation. One RCD switching the second can be done but you need to have some discrimination (possibly a time delay RCD).

As you are undoubtedly aware the partially compliant 17th edition boards have a main switch that feed both RCD's.

A cheap way out would be to have a DP 100A switch in a 2 way enclosure and use it to feed both RCD's? Mark it up as main switch and everyone is happy !
 
All installations should have a single point of isolation. One RCD switching the second can be done but you need to have some discrimination (possibly a time delay RCD).

As you are undoubtedly aware the partially compliant 17th edition boards have a main switch that feed both RCD's.

A cheap way out would be to have a DP 100A switch in a 2 way enclosure and use it to feed both RCD's? Mark it up as main switch and everyone is happy !

Thanks Phil....there is a 100A Hager 2-pole switch on the tails so we're hunky-dory there. I've not had the covers off the CUs (there are 2) so I'll need to check if they share any common bars inside. The board here is undoubtedly 16th Edition.....I need to take a peek inside tomorrow.
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cornwall

Thread Information

Title
CU - RCDs as the main switch?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
steamboatwilly,
Last reply from
steamboatwilly,
Replies
2
Views
1,753

Advert