Update on my Mum's electrics, opened the hatch and was showered with a load of thick black dust, climbed into the loft after coughing my guts up/recovering vision to discover all the roof lining (what ever it was used in the 30's) has disintegrated leaving a thick black layer of crap over everything
So i didn't even bother (have the inclination) to locate the junction boxes etc. So you'll all be pleased to hear her £50 wallpaper is safe for now
On another note had my first "call out" today to my Dad's house as his lights have been tripping intermittently for the last couple of weeks, got there and everything was on so asked him what works he had done recently (reading the forums for that thumbsup) to which he replied new down lights in kitchen and extractor, so tested the board all fine, so linked out the light circuit and went testing had continuity (180ohms on l/e) but couldn't trace the fault.
By this time it was getting dark so put the line back into the mcb switched on and main switch tripped, main switch back on tried a different sequence ring main tripped the main switch (old wylex dial type rcd)

, main switch on another different sequence on for a bit boiler mcb trips the rcd
So try to test the ring mains (4 different circuits on the ground floor, i don't have a wander lead and everything trips in seconds), find four inch screws in the socket cover pull the socket and it moves about a centimetre due to **** cabelling, great, so bin that idea
By this point its dark I've discovered my nephew has knackered my 5 function 900 lumens torch (its cool for kids flashes/pulses etc etc), I've knackered the bulb on my maglite switching it from standing to putting the top cover on :madass: so I'm left with a poxy 1aaa torch that he has in the house. So thought i'd check the forums or internet search at which point I remembered he lives in the middle of the countryside and there's no phone signal nor can I get wifi as his electric keeps tripping
Drive down the road and phone a friend (qualified spark) to describe the fault (should also mention functional test doesn't work on the RCD) and we come to agreement that the RCD may be kaput, manage to get hold of his friend who did the down lights (qualified spark) who described the electrics as a mess and how the down lights took forever to do due the general state of the electrics and he thinks it may be the rcd as well or my dad hasn't fessed up to something
Go back and try the extremes again, find a dual dimmer switch behind a curtain and get from my Dad oh yeh I changed that when I moved in took me ages to do as I couldn't remember how the wires went in, open switch pull the cables and the common from the bottom to top of switch is connected by a single strand and the screw has been battered

strip an re terminate,switch on main switch flick on MCB's and it stays on
Was a bit hairy at moments (when I nearly told him to book into a hotel till I got a new CU) but enjoyed it and learnt a lot of lessons. Am still trying to work out in my head the sequence/readings as I know I had it right in the area the fault was in, just didn't see the dimmer switch