Hello. Got a bit of sticky situation here.
Got called to check on burning smell and arcing from electricity cupboard. Some power loss been reported too.
Its a first floor flat and the power is coming from cutout downstairs (a very, very old cable looking like a VIR and disapperaring behind the board)
Found some charring on the neutral, i suspect that there will be a loose connection inside one of those metal casings.
But i`m not really up for working on it live.
03032016664.jpg

Downstairs flat is owned by different people, we managed to access it and tried to isolate the supply to upstairs, but found that:
03032016663.jpg
There is one service head, one 100A fuse that feeds the meter - for downstairs flat.
Then is the red cable on the left, is leaving the cutout from the side (not from any of the remaining fuses, unless there is some connection inside the cutout?), goes into henley block and splits into dodgy vir cable for flat upstairs, and dodgy vir cable powering flat next door.
If it was one fuse per flat i could call the fairies and sort it out quickly, but thats a bit too much for me.

Informed the customer that there is no way to safely isolate and he should get the UK power network or electrity supplier to sort it out.
He called both but they refuse doing the job.
Not sure what to do now. Advised the guy to write a recorded paper letter and ask for reply on the paper too, in case something goes in flames before.
 
Hello. Got a bit of sticky situation here.
Got called to check on burning smell and arcing from electricity cupboard. Some power loss been reported too.
Its a first floor flat and the power is coming from cutout downstairs (a very, very old cable looking like a VIR and disapperaring behind the board)
Found some charring on the neutral, i suspect that there will be a loose connection inside one of those metal casings.
But i`m not really up for working on it live.
View attachment 31777

Downstairs flat is owned by different people, we managed to access it and tried to isolate the supply to upstairs, but found that:
View attachment 31778
There is one service head, one 100A fuse that feeds the meter - for downstairs flat.
Then is the red cable on the left, is leaving the cutout from the side (not from any of the remaining fuses, unless there is some connection inside the cutout?), goes into henley block and splits into dodgy vir cable for flat upstairs, and dodgy vir cable powering flat next door.
If it was one fuse per flat i could call the fairies and sort it out quickly, but thats a bit too much for me.

Informed the customer that there is no way to safely isolate and he should get the UK power network or electrity supplier to sort it out.
He called both but they refuse doing the job.
Not sure what to do now. Advised the guy to write a recorded paper letter and ask for reply on the paper too, in case something goes in flames before.

Really?

The last instance I had of something similar, I called UK PN on the customers behalf, then turned off their CU - UK PN were there within the hour, replaced the head and everyone was happy!
 
IMO the DNO should be responsible for that cut out, also looks like a fused neutral,call them back. I am surprised they would not attend, after all it is before the supply meter.
 
Maybe your customer, when he called the DNO wasn't a technical person and gave them the wrong info, why don't you as an electrician call them on your customer's behalf?
 
  • Like
Reactions: 2 people
If that neutral starts to float there's going to be tears. I'd contact the DNO as a sparky and explain the issue to them and don't take 'no' for an answer.
 
My last advice to the customer was to call UKPN and the electricity supplier, mentioning past inspection by an electrician and possible loose connection and overheating on their part of installation. If they refuse any action to get their answer in writing.

DNO people were apparently there and said that they are dealing with the part only up to the service head and the rest is not their business.
Electricity provider (not sure who) refused to send someone out after a phone call (and suggested to call DNO!).
 
Last edited:
Informed the customer that there is no way to safely isolate and he should get the UK power network or electrity supplier to sort it out.
He called both but they refuse doing the job.
Not sure what to do now. Advised the guy to write a recorded paper letter and ask for reply on the paper too, in case something goes in flames before.

I think you have really failed here is it too much trouble for you to call the DNO and report the fault, you can provide a far better report to the DNO using the correct terminology for the problem than your customer can
 
Like Murdoch the last time I made this call DNO were out in a couple of hours.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
wild east london

Thread Information

Title
dangerous meter tails
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
amlu,
Last reply from
ferg,
Replies
7
Views
160

Advert