DurhamSparky

just checking my design cal cs for a industrial unit..

Unit is 40kva

so 40 KVA = 32KW (40 x 0.8PF)

32kw / (1.732x400)

32000/692.8 = 46.18a Per Phase...

there is x2 of them been installed in the unit.... Sweet..... Need to check NEDL supply arrangements as other loads in unit will be lighting and small power to office and Security systems...!! hmmmmmmmmmm

hopefully it will be on 125A incomers not just 100A
 
cheers...!! either way i need 125A incomers at the DNO incoming...!! just awaiting the reply from NEDL as to there loading
 