just checking my design cal cs for a industrial unit..
Unit is 40kva
so 40 KVA = 32KW (40 x 0.8PF)
32kw / (1.732x400)
32000/692.8 = 46.18a Per Phase...
there is x2 of them been installed in the unit.... Sweet..... Need to check NEDL supply arrangements as other loads in unit will be lighting and small power to office and Security systems...!! hmmmmmmmmmm
hopefully it will be on 125A incomers not just 100A