ok this q come up in college. And we couldn get to a conclusion.

Max dis time : 0.4s......

TT system , not possible ( high Ze).

So must have rcd to obtain 0.4s...rcd testing , : must operate in 0.4 s @ x 5 current.

However bs7671 states disconection time for TT system as 0.2 secs ? ( portable equipment) .

Why isnt the rcd time for TT 0.2 secs @ 5 x current ?
 
ok so basically its this? :

times : 0.4 for TN : 0.2 for TT .

So TT : 40 ms for rcd @ 5 x current ( 0.04) < 0.2 (200) ?
 
ok so basically its this? :

times : 0.4 for TN : 0.2 for TT .

So TT : 40 ms for rcd @ 5 x current ( 0.04) < 0.2 (200) ? Yes, 40ms < 200ms; 415.1.1

For non RCD protected circuits, faults to earth are 0.4s (400ms) for TN, 0.2s (200ms) for TT; Table 41.1, so yes, your're right there.

With RCD, @ 1 x In, clear fault within 200ms, TN or TT (someone check that for me!)

(BRB refs)
 
For non RCD protected circuits, faults to earth are 0.4s (400ms) for TN, 0.2s (200ms) for TT; Table 41.1, so yes, your're right there.

With RCD, @ 1 x In, clear fault within 200ms, TN or TT (someone check that for me!)

(BRB refs)

Yeah : 1In 200ms : 5In 40ms ....i think . ...ok , cant believe nobody in college picked up on tha...lol
 
And the next question is "how does an RCD to BS 61008/61009 comply with a 0.2 second disconnection time?"

The answer is in the note at the foot of table 41.1 and then the additional time/current figures for RCD's in Appendix 3 of BS 7671
 