Discuss Disconection times in the UK Electrical Forum area at ElectriciansForums.net
daiplayer
ok this q come up in college. And we couldn get to a conclusion.
Max dis time : 0.4s......
TT system , not possible ( high Ze).
So must have rcd to obtain 0.4s...rcd testing , : must operate in 0.4 s @ x 5 current.
However bs7671 states disconection time for TT system as 0.2 secs ? ( portable equipment) .
Why isnt the rcd time for TT 0.2 secs @ 5 x current ?
ok so basically its this? :
times : 0.4 for TN : 0.2 for TT .
So TT : 40 ms for rcd @ 5 x current ( 0.04) < 0.2 (200) ? Yes, 40ms < 200ms; 415.1.1
For non RCD protected circuits, faults to earth are 0.4s (400ms) for TN, 0.2s (200ms) for TT; Table 41.1, so yes, your're right there.
With RCD, @ 1 x In, clear fault within 200ms, TN or TT (someone check that for me!)
(BRB refs)
(BRB refs)
Yeah : 1In 200ms : 5In 40ms ....i think . ...ok , cant believe nobody in college picked up on tha...lol
And the next question is "how does an RCD to BS 61008/61009 comply with a 0.2 second disconnection time?"
The answer is in the note at the foot of table 41.1 and then the additional time/current figures for RCD's in Appendix 3 of BS 7671
Reply to Disconection times in the UK Electrical Forum area at ElectriciansForums.net
On a TT system the rcd must operate withing 0.2 seconds for many circuits. Why when we test rcd's does it not say 300ms for TN systems or 200 ms...
Hi all, just a quick one regarding RCD disconnection times. So for non rcd protected circuits disconnection times of 0.4 / 5 seconds and 0.2 /...
5K
I was asked to go and take a look at a generator set up by a marquee company yesterday to do some testing. It was a brand new JCB 65QS with...
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
6K