Thought I'd try out this ElectricalOM software for a new installation I'm designing. However come up with abit of an issue with the discrimination on 2 of the devices. Single phase sub feed from DB2 (60898 type c 63A 10kA) to DB3, Final circuit from DB3 (61009 30mA 32A type c 10kA RCBO)

Time v Current curve for the devices shows no discrimination for over current protection.



Any ideas or advice?






View attachment 35356

View attachment 35355

View attachment 35357
 
Trouble is I've got 15 of these DBs fed from DB2, that's a hell of a lot of switch fuses.
 
Using two circuit breakers in series the upstream device would have to be in the region of 125A to fully discriminate with the 32A.
 
Thought I'd try out this ElectricalOM software for a new installation I'm designing. However come up with abit of an issue with the discrimination on 2 of the devices. Single phase sub feed from DB2 (60898 type c 63A 10kA) to DB3, Final circuit from DB3 (61009 30mA 32A type c 10kA RCBO)

Time v Current curve for the devices shows no discrimination for over current protection.



Any ideas or advice?






View attachment 35356

View attachment 35355

View attachment 35357


Hi, that's a lot of tiers, try reducing, also you need to ensure your fault current analysis is correct.
 
You nead to use an mccb board or as Dave and Lee says fuse boards to the supply distribution circuits so you can get discrimination
 
Red-Spot fuse board fitted with BS88's would normally sort it. Just be weary though as some combinations of fuses and MCBs still won't fully discriminate.
 