Would be surprised if pumping down to release the high and low pressure lines is not covered by Fgas regs.
You would need to be competent at pumping down, you would need gauges to make sure you had reached vacuum in the low and high pressure side and you would need to confirm the receiver has the capacity to handle all the gas in the pipes. Many systems are not expanded so receiver capacity is as it is, i.e. big enough. But some multi- systems cannot handle all the gas by pumping down so has to be recovered to a bottle. the OP just shows one evaporator, who knows what else is out there.... In the UK and EU - the actual total gas installed is shown on the data plate, it should show one figure for shipped and another for additional gas added for that particular installation. The Fgas eng needs to ensure pumping down the total gas is doable.
Electricians - know your limits ! - lol