I have a series of Henley blocks suppling db’s. Henly block are protected by an bs88 63amp fuse. We have a 2.5mm 6181y cable feeding a isolator which in turns feeds a fire alarm panel, this 2.5mm cable is around 0.5 metre long and within the fire alarm isolator, there is a 20amp fuse. Would this be overrated or due to in the 2m rule be ok? Thanks
 
It may satisfy overcurrent requirements but possibly not fault or short circuit requirements.
 
Good Morning

I have a series of Henley blocks suppling db’s. Henly block are protected by an bs88 63amp fuse. We have a 2.5mm 6181y cable feeding a isolator which in turns feeds a fire alarm panel, this 2.5mm cable is around 0.5 metre long and within the fire alarm isolator, there is a 20amp fuse. Would this be overrated or due to in the 2m rule be ok? Thanks