Rockingit

-
Mentor
Esteemed
Arms
Supporter
Reaction score
6,235
Due to a damaged underground SWA that would normally feed a sub main, I may have to place a genset temporarily to run a small kids funfair area at a park (so I assume lots of star>delta motors and variable speed controllers)

I’ve three options for sizing this:

1. Add it all up and work with maximum;
2. Apply some form of diversity or
3. Assume that the existing CPD rating will suffice as an indicator and work with that value.

The tricky bit of course is that a generator behaves slightly differently to a DNO supply.

Thoughts?
 
Closer inspection revealed that the whole lot is fed via a 125a main isolator with the single largest device being a 63/3 so I’m just going to drop a 100kva set in there which I know will cover it all comfortably.
 

Reply to Diversity for a funfair? in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock