Due to a damaged underground SWA that would normally feed a sub main, I may have to place a genset temporarily to run a small kids funfair area at a park (so I assume lots of star>delta motors and variable speed controllers)

I’ve three options for sizing this:

1. Add it all up and work with maximum;
2. Apply some form of diversity or
3. Assume that the existing CPD rating will suffice as an indicator and work with that value.

The tricky bit of course is that a generator behaves slightly differently to a DNO supply.

Thoughts?
 
What do you get for options 1 and 3?
 
Closer inspection revealed that the whole lot is fed via a 125a main isolator with the single largest device being a 63/3 so I’m just going to drop a 100kva set in there which I know will cover it all comfortably.
 