"I would be tempted to use someone with the necessary technical expertise to get this project up and running to be honest. Less risk than designing by web search, and you will end up with a good solution in less time."
I thought I had found someone else who was well qualified. (Electrical engineering degree). But he told me to buy a timer which was rated at 3,000 watts and that it would cope with powering the ballasts without having to use a contactor. But when I got the timer it says it's rated at 2,300 watt. Also, he gave me instructions for wiring it up which are not complete. (Where do the wires for the contactor switch go?). He also told me that I did not need a breaker because the fuse in the plug will suffice. But as far as I'm aware it's only UK plugs that have fuses. I intend to sell this thing worldwide.
So how do I find someone with the necessary expertise and how do I know they are a) competent and b) really want to help me. c) affordable
"...First off in the USA the voltage is 240/120,..."
Yes. I'd spotted that. The 240 is mainly for commercial though isn't it? A plug socket in a domestic setting will be 120v. Correct?
You do need to look closely at the load for the USA version, as it is nudging the 15A boundary. Is it intended to connect with a NEMA 5-15? If so, if the pf is good you're just in for running load with 5% below nominal as per NEC, (10 x 160 / 114 = 14A) but if the ballast will operate at say 100V it will go over the 15A. An MCB won't stop that happening and you would have to go up to a 5-20 which is less convenient for domestic users.